AutoDesk RVT_ELEC_01101 Exam - Topic 5 Question 17 Discussion

Posted by Cherri on Jul 16, 2026 at 02:13 AM

Refer to exhibit.

An electrical designer expects the total connected load on the switchboard to be 4000VA. but Revit Indicates a total connected load of 3606VA. What Is the cause of the discrepancy?

Suggested Answer: B

In the exhibit, the designer expects the total connected load to equal the sum of the 4 motor loads:

4 motors 1000 VA each = 4000 VA expected

However, Revit is showing a Total Connected Load of 3606 VA instead.

This difference occurs because Revit applies Motor Demand Factors automatically when a load classification is set to ''Motor.'' Demand factors modify the total connected load based on electrical engineering rules.

Revit documentation confirms:

''Assign demand factors to load classifications.''

''Demand loads can be shown on panel schedules.''

In the exhibit, the Load Classification shows Motor with a Demand Factor of 117.87%, which modifies the connected load values in the switchboard totals.

Revit is therefore calculating the effective connected load based on the applied demand factor, not a simple arithmetic sum. That is why the panel's connected load number 4000 VA.


Get Premium RVT_ELEC_01101 Questions as Interactive Web-Based Practice Test or PDF Real Exam Format Detailed Explanations Instant Access Get Your Practice Test
12 comments · newest first
PE
Pete 1 month ago
C makes sense too. Feed through lugs could affect the total load reading.
DI
Diego 1 month ago
I lean towards B. The motor demand factor might be lowering the load.
LA
Latricia 1 month ago
I think it's A. Different voltage settings can cause discrepancies.
TH
Thea 2 months ago
I’m leaning towards D, true and reactive load settings matter a lot.
WI
Winfred 2 months ago
Definitely C, those feed through lugs can mess things up.
BE
Ben 2 months ago
Wait, how can the load be so off? That’s surprising!
TE
Terina 2 months ago
I disagree, it’s probably B with the motor demand factor.
DA
Dalene 2 months ago
I think it's option A, voltage mismatch could cause that.
JA
James 2 months ago
I vaguely recall something about true load and reactive load settings, but I can't remember how they impact the total connected load.
LI
Lizbeth 3 months ago
I wonder if the feed through lugs could be causing the difference. I feel like I read about that in our notes.
VA
Vallie 3 months ago
I think the motor demand factor could definitely play a role in this discrepancy. We practiced a similar question on that.
PA
Paola 3 months ago
I remember something about voltage settings affecting load calculations, but I'm not sure if that's the main issue here.
0/2000 characters

Save Cancel