Annual testing for a 1,500 gpm (5,677 L/min) at 80 psi (1.4 bar) fire pump supporting an attached sprinkler system
demand of 1,800 gpm (6,813 L/min) at 100 psi (6.9 bar) is being conducted. The flow test of the fire pump must
achieve what minimum flow rate and discharge pressure?
For annual testing of fire pumps, NFPA standards require the pump to be tested at its rated capacity and pressure, as well as at 150% of its rated capacity at a correspondingly lower pressure. In this scenario, the minimum flow rate required for the test is the demand of the attached sprinkler system, which is 1,800 gpm at 100 psi, to ensure the pump can meet or exceed the system's highest demand.