At what minimum pressure would automatic sprinkler piping be hydrostatically tested if the maximum system pressure is 175 psi (12 bar)?

Show Suggested Answer Hide Answer
Suggested Answer: B

According to NFPA 13, Standard for the Installation of Sprinkler Systems, all sprinkler piping must undergo a hydrostatic test to verify its strength and leak resistance.

Hydrostatic testing must be conducted at a pressure of 200 psi (13.8 bar) or 50 psi (3.4 bar) greater than the system's maximum working pressure, whichever is higher.

Since the maximum system pressure is 175 psi, the test pressure must be at least 200 psI .

175 psi (A) is the system pressure, not the test pressure.

225 psi (C) and 250 psi (D) exceed the required test pressure.


NFPA 13, Section 25.2.1.1: Hydrostatic test requirements for sprinkler piping.

Contribute your Thoughts:

Erinn
3 days ago
You know, I bet they're just trying to trick us with this question. The answer is definitely A, 175 psi (12 bar). Easy peasy.
upvoted 0 times
...
Dalene
5 days ago
Hmm, I'm gonna go with D. Better safe than sorry, right? 250 psi (17 bar) sounds about right.
upvoted 0 times
...
Laticia
21 days ago
Why do you think it's B)?
upvoted 0 times
...
Tesha
24 days ago
I disagree, I believe the correct answer is B) 200 psi.
upvoted 0 times
...
Ty
26 days ago
Dude, if the max system pressure is 175 psi, then the test pressure should be at least 250 psi (17 bar). Safety first, am I right?
upvoted 0 times
...
Laticia
27 days ago
I think the answer is A) 175 psi.
upvoted 0 times
...
Carmelina
1 months ago
Nah, I'm pretty sure it's C, 225 psi (15.5 bar). Gotta test it a little higher than the max system pressure, you know?
upvoted 0 times
...
Marguerita
1 months ago
I think the answer is B, 200 psi (13.8 bar). That's the standard minimum pressure for hydrostatic testing, right?
upvoted 0 times
Paulina
18 days ago
A) 175 psi (12 bar)