At what minimum pressure would automatic sprinkler piping be hydrostatically tested if the maximum system pressure is 175 psi (12 bar)?

Show Suggested Answer Hide Answer
Suggested Answer: B

According to NFPA 13, Standard for the Installation of Sprinkler Systems, all sprinkler piping must undergo a hydrostatic test to verify its strength and leak resistance.

Hydrostatic testing must be conducted at a pressure of 200 psi (13.8 bar) or 50 psi (3.4 bar) greater than the system's maximum working pressure, whichever is higher.

Since the maximum system pressure is 175 psi, the test pressure must be at least 200 psI .

175 psi (A) is the system pressure, not the test pressure.

225 psi (C) and 250 psi (D) exceed the required test pressure.


NFPA 13, Section 25.2.1.1: Hydrostatic test requirements for sprinkler piping.

Contribute your Thoughts:

0/2000 characters
Pansy
2 months ago
The standard is indeed 200 psi for testing.
upvoted 0 times
...
Shawna
2 months ago
I thought it was 225 psi? Seems high.
upvoted 0 times
...
Norah
2 months ago
Definitely B, can’t risk it with lower pressure!
upvoted 0 times
...
Scarlet
3 months ago
It’s usually 1.5 times the max pressure, so 200 psi sounds right.
upvoted 0 times
...
Jackie
3 months ago
Wait, why would it be 250 psi? That seems excessive.
upvoted 0 times
...
James
3 months ago
I thought it was 250 psi, but I might be mixing it up with another type of system. I need to double-check the guidelines.
upvoted 0 times
...
Hildegarde
3 months ago
I feel like the answer might be 225 psi, but I can't recall if that's the standard for hydrostatic testing.
upvoted 0 times
...
Julio
4 months ago
I remember a practice question where we had to calculate the test pressure based on the system pressure. I think it was around 200 psi for a system like this.
upvoted 0 times
...
Laila
4 months ago
I think the minimum pressure for hydrostatic testing is usually 1.5 times the maximum system pressure, but I'm not entirely sure how that applies here.
upvoted 0 times
...
Marguerita
4 months ago
Ah, I remember this from the lecture. The hydrostatic test pressure is typically 50% higher than the maximum system pressure. So if the max is 175 psi, the minimum test pressure would be 175 + (0.5 x 175) = 262.5 psi. I think the answer is D.
upvoted 0 times
...
Tashia
4 months ago
I'm a bit confused on this one. I know the hydrostatic test pressure needs to be higher than the maximum system pressure, but I'm not sure of the exact relationship. I'll have to review my notes and try to reason this out.
upvoted 0 times
...
Linwood
4 months ago
Okay, let me see if I can figure this out. The maximum system pressure is 175 psi, so the hydrostatic test pressure needs to be higher than that. I'm thinking the answer is probably B or C, but I'll have to double-check the typical pressure increase for hydrostatic testing.
upvoted 0 times
...
Meaghan
5 months ago
Hmm, I'm a little unsure about this one. I know the hydrostatic test pressure is usually higher than the maximum system pressure, but I'm not sure by how much. I'll have to think this through carefully.
upvoted 0 times
...
Kayleigh
5 months ago
This one seems pretty straightforward. The question is asking for the minimum pressure for hydrostatic testing, and the maximum system pressure is 175 psi, so I think the answer is A.
upvoted 0 times
...
Truman
7 months ago
Alright, time to break out the pressure gauge and give it a good ol' hydrostatic test! Woohoo, let's do this!
upvoted 0 times
Tegan
5 months ago
B) 200 psi (13.8 bar)
upvoted 0 times
...
Alisha
7 months ago
A) 175 psi (12 bar)
upvoted 0 times
...
...
Erinn
7 months ago
You know, I bet they're just trying to trick us with this question. The answer is definitely A, 175 psi (12 bar). Easy peasy.
upvoted 0 times
...
Dalene
7 months ago
Hmm, I'm gonna go with D. Better safe than sorry, right? 250 psi (17 bar) sounds about right.
upvoted 0 times
Yolando
7 months ago
I agree, D seems like the safest option for hydrostatic testing.
upvoted 0 times
...
Fidelia
7 months ago
I think D is a good choice too. It's always better to be safe.
upvoted 0 times
...
...
Laticia
8 months ago
Why do you think it's B)?
upvoted 0 times
...
Tesha
8 months ago
I disagree, I believe the correct answer is B) 200 psi.
upvoted 0 times
...
Ty
8 months ago
Dude, if the max system pressure is 175 psi, then the test pressure should be at least 250 psi (17 bar). Safety first, am I right?
upvoted 0 times
Cassie
7 months ago
D) 250 psi (17 bar)
upvoted 0 times
...
Shannon
7 months ago
A) 175 psi (12 bar)
upvoted 0 times
...
...
Laticia
8 months ago
I think the answer is A) 175 psi.
upvoted 0 times
...
Carmelina
8 months ago
Nah, I'm pretty sure it's C, 225 psi (15.5 bar). Gotta test it a little higher than the max system pressure, you know?
upvoted 0 times
...
Marguerita
8 months ago
I think the answer is B, 200 psi (13.8 bar). That's the standard minimum pressure for hydrostatic testing, right?
upvoted 0 times
Linette
7 months ago
C) 225 psi (15.5 bar)
upvoted 0 times
...
Glory
7 months ago
Correct! The minimum pressure for hydrostatic testing is typically 1.5 times the maximum system pressure.
upvoted 0 times
...
Lisbeth
7 months ago
B) 200 psi (13.8 bar)
upvoted 0 times
...
Sharmaine
7 months ago
No, the minimum pressure for hydrostatic testing is higher than the maximum system pressure.
upvoted 0 times
...
Paulina
8 months ago
A) 175 psi (12 bar)
upvoted 0 times
...
...

Save Cancel