What is the floor loading requirement for a Rated-3 data center according to ANSI/TIA-942?
Suggested Answer: C
Get Premium CDCS Questions
as Interactive Web-Based Practice Test or PDF
Real Exam Format
Detailed Explanations
Instant Access
Get Your Practice Test
ANSI/TIA-942 specifies minimum floor live load capacities based on Rated levels:
Rated-1/2: ~7.2--8.4 kPa
Rated-3: 12 kPa
Rated-4: 15 kPa
These values ensure raised floors can support racks, cabling trays, cooling units, and maintenance loads without structural compromise. For Rated-3, concurrent maintainability requires higher floor robustness to handle additional infrastructure.
Therefore, the correct requirement is 12 kPa.