What is the redundancy setup shown in the diagram?

Show Suggested Answer Hide Answer
Suggested Answer: B

The diagram shows three UPS modules, each 100 kW, connected in parallel to support a 100 kW IT load. That means:

One module (100 kW) can support the load (N).

Two additional modules are installed as redundancy.

This equals N+2 redundancy.

2+N+1 and 2(N+1) imply dual active paths not shown.

N+N+N is not an industry term.

Thus, the correct redundancy level is N+2.