Which class of UPS is ideal for data centers?

Show Suggested Answer Hide Answer
Suggested Answer: C

IEC 62040 defines UPS topologies:

VFD: Line-interactive; dependent on mains.

VI: Stabilizes voltage but not frequency.

VFI: Double-conversion online; fully isolates output from mains fluctuations.

Data centers require continuous, clean, and stable power. VFI is the only topology that protects against both voltage and frequency disturbances, meeting ANSI/TIA-942 Rated-3/4 requirements.

Thus, VFI is the ideal UPS class.